The only bar in town recently changed hands and is on a shoestring budget. We're trying to help them out. The garbage truck caught the 200 AMP single phase 124TB B-Line meter panel and jammed the cover into the meter socket bussing with arcing ensuing. We pounded the enclosure straight and screwed the cover back on, but found a chunk of black plastic that is mostly likely a piece of the meter socket base. The utility has a locking ring on the meter, but even without it we would be reluctant to pull the meter if the base may be broken. We plan to get a new panel and most likely rob parts to replace any damaged components. The utility will re-energize the service without a permit so long as we don't replace the enclosure. We are concerned that we may find damage or corrosion which mandates replacing the panel, which will likely trigger a permit and inspection requirement. We want to be prepared lest the bar loses needed revenue.
I seriously doubt our local jurisdiction has a clue what they are doing, but I have seen the case in other jurisdictions where all the 120 VAC 15 AMP receptacles had to be two wire and fed with an upstream GFCI receptacle. We do not want any part of rewiring the building. My thought is to replace the two main disconnect circuit breakers with GFCI circuit breakers, but I'm unfamiliar and don't quite understand how a two pole GFCI breaker works.
The 200 AMP single phase meter panel feeds a 125 AMP four space CH4R load center with twin 60 AMP two pole CH260 miniature circuit breakers. The load center is the tan toggle plug on Cutler Hammer series. Downstream of each breaker there are only three conductors, L1, L2 and neutral (no ground). The CHGF breakers I see have two load lugs and a white pig tail. I also see Square D QO GFCI two pole breakers figured similarly.
As I said I don't understand how two pole GFCI circuit breaker function. Does anyone know if either or both of these breakers will feed both 120 and 240 loads simultaneously without tripping the GFCI? I would have thought you need a circuit breaker with neutral line and load connections.
I seriously doubt our local jurisdiction has a clue what they are doing, but I have seen the case in other jurisdictions where all the 120 VAC 15 AMP receptacles had to be two wire and fed with an upstream GFCI receptacle. We do not want any part of rewiring the building. My thought is to replace the two main disconnect circuit breakers with GFCI circuit breakers, but I'm unfamiliar and don't quite understand how a two pole GFCI breaker works.
The 200 AMP single phase meter panel feeds a 125 AMP four space CH4R load center with twin 60 AMP two pole CH260 miniature circuit breakers. The load center is the tan toggle plug on Cutler Hammer series. Downstream of each breaker there are only three conductors, L1, L2 and neutral (no ground). The CHGF breakers I see have two load lugs and a white pig tail. I also see Square D QO GFCI two pole breakers figured similarly.
As I said I don't understand how two pole GFCI circuit breaker function. Does anyone know if either or both of these breakers will feed both 120 and 240 loads simultaneously without tripping the GFCI? I would have thought you need a circuit breaker with neutral line and load connections.