I have a 3-phase, 480 to 208 transformer in the first compartment of a control panel enclosure that has three compartments. For simplicity I'll call these Panel 1, Panel 2, and Panel 3, with Panel 1 being the one housing the transformer and a Main disconnect switch. The output of this transformer gives me 3 hots and one neutral which I can use to supply 120VAC to three circuits in Panel 2. The neutral would be bonded to earth ground at the transformer.
The problem is the third compartment, or panel 3. Panels 2 and 3 have to be able to turn off independently because they will power two different machines. If one panel is turned off, the other should keep working. I want to supply 120VAC for outlets along the machines to both panels, yet keep one live if the other is off. Each panel has its own disconnect switch. PANEL 1 WOULD ALWAYS BE ON. It would be turned off only if both machines need to be off (like during maintenance)
I thought of a way of doing this by using 3-pole contactors mounted inside Panel 1; one for Panel 2 and one for Panel 3. If Panel 2 is turned on, the 24VAC from that panel would energize the coil of the contactor and supply 120 VAC to that panel only. Same goes for Panel 3 if I turn on that panel.
However, the neutral wire would be shared. Will there a problem there?. Should I use a 4-pole contactor or transfer switch? Any transients to worry about?. Please see attached image.
Thank you
The problem is the third compartment, or panel 3. Panels 2 and 3 have to be able to turn off independently because they will power two different machines. If one panel is turned off, the other should keep working. I want to supply 120VAC for outlets along the machines to both panels, yet keep one live if the other is off. Each panel has its own disconnect switch. PANEL 1 WOULD ALWAYS BE ON. It would be turned off only if both machines need to be off (like during maintenance)
I thought of a way of doing this by using 3-pole contactors mounted inside Panel 1; one for Panel 2 and one for Panel 3. If Panel 2 is turned on, the 24VAC from that panel would energize the coil of the contactor and supply 120 VAC to that panel only. Same goes for Panel 3 if I turn on that panel.
However, the neutral wire would be shared. Will there a problem there?. Should I use a 4-pole contactor or transfer switch? Any transients to worry about?. Please see attached image.
Thank you