Can you have a control cabinet with a 480 source to a disconnect AND a 120 source to the cabinet that will still be live even if you turn off the disconnect?
430.113. Energy from more than one source
Motor and motor-operated equipment receiving electric energy
from more than one source shall be provided with disconnecting
means from each source of electric energy immediately
adjacent to the equipment served. Each source shall
be permitted to have a separate disconnecting means.
Where multiple disconnecting means are provided, a permanent
warning sign shall be provided on or adjacent to
each disconnecting means.
Exception No. 1: Where a motor receives electric energy
from more than one source, the disconnecting means for the
main power supply to the motor shall not be required to be
immediately adjacent to the motor, provided that the controller
disconnecting means is lockable in accordance with 110.25.
Exception No. 2: A separate disconnecting means shall
not be required for a Class 2 remote-control circuit conforming
with Article 725, rated not more than 30 volts, and
isolated and ungrounded.
Certainly, it's done all the time. But depending on which standards apply, you must at the very least clearly identify that there are multiple sources of energy in the cabinet, and/or use a different color of wire to identify it (usually yellow), and/or interlock it via an aux contact of the 480V disconnect, and/or provide its own disconnect that is interlocked with the enclosure door. NFPA-79, which applies to industrial control panels for machinery, will require you to use one of the door interlocking options, plus the labeling and wire color.Can you have a control cabinet with a 480 source to a disconnect AND a 120 source to the cabinet that will still be live even if you turn off the disconnect?
Can you have a control cabinet with a 480 source to a disconnect AND a 120 source to the cabinet that will still be live even if you turn off the disconnect?
Certainly, it's done all the time. But depending on which standards apply, you must at the very least clearly identify that there are multiple sources of energy in the cabinet, and/or use a different color of wire to identify it (usually yellow), and/or interlock it via an aux contact of the 480V disconnect, and/or provide its own disconnect that is interlocked with the enclosure door. NFPA-79, which applies to industrial control panels for machinery, will require you to use one of the door interlocking options, plus the labeling and wire color.