Thoughts on 2020 NEC compliance? These are two grouped disconnects - is that different from a meter main with two breakers?

Side question Q2150MRBE disconnect (if anyone is familiar) - can it be reversed to have line side on the bottom and load up top

230.71(A) 230.85(B)
Screenshot 2025-03-02 at 7.49.23 PM.png
 
Looks good to me. We did many of these when meter-mains with separate compartments for the mains were unavailable.

If those disconnects are not marked "Line & Load" at the terminals, I would say you can feed bottom.

Are you on 2020 Code in Florida?
 
Looks good to me. We did many of these when meter-mains with separate compartments for the mains were unavailable.

If those disconnects are not marked "Line & Load" at the terminals, I would say you can feed bottom.

Are you on 2020 Code in Florida?
Yes 2020 code just really started to enforce around May of last year

This job currently has 2 150A panels on a 200A meter/enclosure - the utility engineer had me read off the meter model and told me they will use the same meter as it can read up to 400A