two service drops/one service

Status
Not open for further replies.

bnolen

Member
Due to the price and difficulty in obtaining 600mcm a contractor is wanting to forego a single 600mcm service drop and install two service drops of 4/0 aluminum. Perusing the 2008 NEC now, but thought I would give a shout out to the experts. NEC compliant to do this? Thanks.
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Was the 600 KCMIL going to be Aluminum?

Roger
 

mgookin

Senior Member
Location
Fort Myers, FL
Due to the price and difficulty in obtaining 600mcm a contractor is wanting to forego a single 600mcm service drop and install two service drops of 4/0 aluminum. Perusing the 2008 NEC now, but thought I would give a shout out to the experts. NEC compliant to do this? Thanks.

Why isn't POCO supplying the drop?
 

DeltaFarce

New User
Location
NJ
Why isn't POCO supplying the drop?
I think it's just a little confusion in terminology.

When he says "1 service" he means 1 overhead line from the PoCo.
When he says "2 drops" I believe he means 2 parallel risers from the POA down to the service equipment.

Then the 4/0 parallels will be fine as far as the NEC is concerned.
Yup, it's very common around here to run (2) 2" PVC risers with 4/0 AL for 400A services. Easier than dealing with huge pipe and 600MCM's.
 