We have a building which has two service entrances. The AHJ has already bought off on the idea some time ago, the second service was installed because of capacity and reliability (a computer facility) and also in a part of the building behind a 2 hour fire separation (separate building).
We have several situations where there is an electrical room, with a panelboard from Service A on one wall, and from Service B on another wall. The client told me flatly "it's a code violation to have two different services in a room".
I cannot think of any part of the NEC that forbids panels fed from more than one service in the same room, and in fact this would be common in hospitals, where dual feeds and double ended switchgear are the norm.
Is this a rule, or is this guy just out in space?
We have several situations where there is an electrical room, with a panelboard from Service A on one wall, and from Service B on another wall. The client told me flatly "it's a code violation to have two different services in a room".
I cannot think of any part of the NEC that forbids panels fed from more than one service in the same room, and in fact this would be common in hospitals, where dual feeds and double ended switchgear are the norm.
Is this a rule, or is this guy just out in space?