Two services or one

Status
Not open for further replies.

hhsting

Senior Member
Location
Glen bunie, md, us
Occupation
Junior plan reviewer
In the exhibit below it is shown that service point is at the transformer.

However what if the service point was at the utility meters and utility brought their conductors underground from utility transformer secondary to the utility meters as shown below then would this be one service or more than one services based on attached 230.2 first paragraph where it says “For the purpose of 230.40 exception no. 2….”?


668d34d2d2c6f3d6f0ae4e293eaef24f.jpg


5bb50d01d5b7ad3c5593f1559fe7cf51.jpg
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
NEC doesn't apply to POCO installed conductors but, in theory, the rule would be the same no matter who installed the conductors.
 