I have two services 0ne 120/240 volt and one 3 phase 240 volt side by side ( 2') from each other. can I use one ground rod for the two.
I have two services 0ne 120/240 volt and one 3 phase 240 volt side by side ( 2') from each other. can I use one ground rod for the two.
Is it really two services? Two drops or laterals?
Considering one is single phase and one is three phase, it's a safe bet there are two drops there. That being said, the poco may have tapped the 120/240 single phase service from the 240 volt delta service with a center tap, but I've never seen an odd duck like that.
They are all over around here, lots of 120/240 single phase services supplied by a 120/240 three phase source, with that one customer in the five supplied that utilizes three phase (or something of that nature).Considering one is single phase and one is three phase, it's a safe bet there are two drops there. That being said, the poco may have tapped the 120/240 single phase service from the 240 volt delta service with a center tap, but I've never seen an odd duck like that.
They are all over around here, lots of 120/240 single phase services supplied by a 120/240 three phase source, with that one customer in the five supplied that utilizes three phase (or something of that nature).
If up to six sets of conductors run from a single source to up to six separate disconnecting means (may be more then six individual wires altogether when considering possible parallel conductors) it is considered one service. 120/240 volt single phase and 120/240 three phase both originating at same source is still only one service IMO. Sure you have different number of phases associated with one, but they are still a part of same system.
120/240 single phase and 208/120 three phase by nature have to come from separate sources so if you had that for incoming it would be two services.