hhsting
Senior Member
- Location
- Glen bunie, md, us
- Occupation
- Junior plan reviewer
I have one transformer X which feeds 1000A service disconnect thru underground into electrical room
The transformer X is now in addition going to have another service conductor 400A underground but come up next to the electrical room door outside and thats where the 400A service disconnect is going to be.
The 1000A service feeds building and the 400A service would feed separate canopy gas (as in cooking gas) station 30 feet from the building but its 400A service disco would be right outside building electric room room door on outside wall of building. This is gas utility.
The existing configuration their was one service which fed all the building and the canopy station. The 1000A swbd fed the canopy station. Now they want to have separate service for the canopy gas station so they can meter bill it.
I said to engineer to group the 400A service disconnect with the 1000A service disco in one room so that based on 230.2 first paragraph this can be considered one service.
The engineer came back with saying their is no space inside the electrical room. An inspector from AHJ was sent out to site he came back saying their is no space for 400A main service disco in electrical room.
I said is their way you can relocate equipment to make space and engineer came back saying they dont want to relocate equipment because they have dig concrete floor and since this is gas utility no one knows whats down there and involve cost.
So here I am would anyone have any ideas here or would this fall under 230.2(E) plaques and in this case two utilities service must be provided?
I am the acting plans reviewer for the AHJ and in tough situation.
Thanks
The transformer X is now in addition going to have another service conductor 400A underground but come up next to the electrical room door outside and thats where the 400A service disconnect is going to be.
The 1000A service feeds building and the 400A service would feed separate canopy gas (as in cooking gas) station 30 feet from the building but its 400A service disco would be right outside building electric room room door on outside wall of building. This is gas utility.
The existing configuration their was one service which fed all the building and the canopy station. The 1000A swbd fed the canopy station. Now they want to have separate service for the canopy gas station so they can meter bill it.
I said to engineer to group the 400A service disconnect with the 1000A service disco in one room so that based on 230.2 first paragraph this can be considered one service.
The engineer came back with saying their is no space inside the electrical room. An inspector from AHJ was sent out to site he came back saying their is no space for 400A main service disco in electrical room.
I said is their way you can relocate equipment to make space and engineer came back saying they dont want to relocate equipment because they have dig concrete floor and since this is gas utility no one knows whats down there and involve cost.
So here I am would anyone have any ideas here or would this fall under 230.2(E) plaques and in this case two utilities service must be provided?
I am the acting plans reviewer for the AHJ and in tough situation.
Thanks