I was reviewing my colleagues' electrical design on a project and came across a mechanical equipment that required two 1P branch circuits serving a single equipment. I then wrote to provide a 2P circuit breaker or a two 1P circuit breakers with a handle tie to serve the equipment. However, the design intent of the two circuits was one branch circuit of the mechanical equipment will always operate and the second branch circuit will serve as a standby operation.
The code reference I referenced regarding this scope of work was NFPA 70 (NEC) Article 210.4 "Multiwire Branch Circuits". Is this particular situation considered as a "multiwire branch circuit" if each single pole branch circuit is served with a dedicated neutral? If yes, how can we accomplish this installation in a way to allow the second branch circuit to remain on if the first circuit breaker trips? If not, then would it be acceptable as shown with two 1P circuit breakers with no handle tie?
Thank you.
The code reference I referenced regarding this scope of work was NFPA 70 (NEC) Article 210.4 "Multiwire Branch Circuits". Is this particular situation considered as a "multiwire branch circuit" if each single pole branch circuit is served with a dedicated neutral? If yes, how can we accomplish this installation in a way to allow the second branch circuit to remain on if the first circuit breaker trips? If not, then would it be acceptable as shown with two 1P circuit breakers with no handle tie?