Two small appliances per kitchen?

Eliasc94

Member
Location
Houston, Texas
Occupation
Electrical Field Supervisor
What is the proper interpretation for 210.11 and 210.52? Should we have two small appliance circuits per kitchen? I am supervising a 5000 sq ft house and I ran two circuits to the main kitchen, two to the chef’s kitchen and two to the outdoor kitchen. Each room/area has a sink, cooking equipment and countertop space for food prep.
 

Eliasc94

Member
Location
Houston, Texas
Occupation
Electrical Field Supervisor
Yeah unfortunately I didn’t do the bid for the house and I don’t think my company interprets the code this way. So I likely lost us some money by adding additional circuits where not bid for it. We basically ran dedicated circuits for every installed appliance in the house. It’s been a pain in my ass to be frank.
 

Eliasc94

Member
Location
Houston, Texas
Occupation
Electrical Field Supervisor
FWIW, I would not have run only two Kitchen circuits. At very least the outdoor kitchen would have its own pair with the other two sharing.
Understand, I rarely did housing after my early years of more than enough of them.
Perhaps you misunderstood. I ran 6 circuits in total. 2 to each area I determined that was a “kitchen”.
 
Location
NE (9.06 miles @5.9 Degrees from Winged Horses)
Occupation
EC - retired
Perhaps you misunderstood. I ran 6 circuits in total. 2 to each area I determined that was a “kitchen”.
I got that.

The least would have been…
FWIW, I would not have run only two Kitchen circuits. At very least the outdoor kitchen would have its own pair with the other two sharing.
Understand, I rarely did housing after my early years of more than enough of them.
 
Top