Please confirm my thinking....
Existing Structure "A" has a 400 amp meter, a 200 panel and a 200 amp disconnect feeding Structure "B" via an underground 3" conduit.
Contractor wants to add 2nd 200 amp panel at "B"
(Total load on the two structures will be less than 400 amp)
1st thought was two 200 amp feeders through the 3" conduit but 2017 Code will not allow 2 feeders to separate building.
That led to Plan 1 to install one 400 amp feeder to a j box and tap to the two 200 amp M/B panels.
Plan 2 is to come directly off the meter base installing service conductors to Building B using the Exception 3 to 230.40
Question being:: Can 2 sets of service conductors be installed in the conduit with each set terminating in 200 amp adjacent panels based in the wording in 230.2 classifying two sets 1/0 and larger as one service