Two switches in parallel... will it work ??

Status
Not open for further replies.

randyo

Member
Location
Maryland
you have a heat lamp... in a well house....

If I wired a 120v thermistat "120v switch" and a regular switch in parallel...would that work..

|nnnnnnnn switch nnn|
|nnnnn thermistat nnn|nnn|
................................ (lite)
hhhhhhhhhhhhhhhhhhhhhh|

IF the thermistat kicks, it the light is on
if I flip the switch, the light is on.
What happens if both are on at the same time????

Is there a code violaton with switches in parallel like this???
 

Ed MacLaren

Senior Member
Re: Two switches in parallel... will it work ??

The term "switch" can mean Control Device or Disconnecting Means.

Control devices are routinely connected in parallel where a load must be controlled by more than one actuating mechanism, as in your case.
A basic rule of control is -
On devices in parallel - Off devices in series.

There should be a single disconnecting means ahead of the control devices. I'm not sure of the NEC rule on this, but I'm sure someone will help with that.

Ed
 

curt swartz

Electrical Contractor - San Jose, CA
Location
San Jose, CA
Occupation
Electrical Contractor
Re: Two switches in parallel... will it work ??

Do the n's and h's represent the hots and neutrals? If so why are we switching the neutral?
 

paul

Senior Member
Location
Snohomish, WA
Re: Two switches in parallel... will it work ??

I see a violation if the switch that is used says 'off' when in the open position.
 

luke warmwater

Senior Member
Re: Two switches in parallel... will it work ??

Originally posted by randyo:

What happens if both are on at the same time????
The light will be on.

Is there a code violaton with switches in parallel like this???
Not that I could find. These type of circuts are commonly used in motor control, which I think Ed's post may have been based on.
I've seen and used this type of circut on various situations such as a timeclock and toggle switch to operate a contactor, or a photocell and toggle switch to operate a light fixture.
I believe Ed to be right about the disconnect if it was a motor control circut, 430.74.
If it were fixed electrical space-heating equipment, then 424.19. But under the scope of Article 424, IMO a heat lamp would not count(any other opinions on this?).
IMO you have a branch circut design that works.
 