Two VFDs fed off single breaker

Status
Not open for further replies.

LMAO

Senior Member
Location
Texas
Two identical VFD breakers fed off identical conductors protected by a single breaker...? There shouldn't be an issue as long as conductors are sized appropriately with respect to the main breaker, correct?


.................
/------------breaker------------VFD------------motor
main breaker
.................
\------------breaker------------VFD------------motor
 

Cow

Senior Member
Location
Eastern Oregon
Occupation
Electrician
I don't see an issue, but I'd also make sure the breaker hasn't been oversized beyond the manufacturers recommended breaker size for the drives.

EDIT: I didn't notice the individual OCPD in line with each VFD, so disregard my post. You should be fine.
 