Dale Hayes
Senior Member
Inside a control panel there is a 480v, 500Amp, 3-phase circuit breaker with several contactors attached to a heater load. There is also a 120V, 1-phase control circuit supplied from a 480V to 120V, 500VA 1-phase control transformer.
For grounding purposes there is a #2 GA grounding lug at the panel grounding bar - sized for the 500Amp circuit breaker .
The panel enlosure itself is supplied with (3) grounding stud connection points for (2) grounding wires.
One grounding wire is attached from a stud on the inner wall of the enclosure to the enclosure door and (1) wire is attached from the same stud at the inner wall of the enclosure to the removeable inner panel.
For the (2) grounding wires that connect the enclosure to the door and to the inner panel - what wire size is needed?
Are these (2) "enclosure/door/panel" grounding wires sized for the 500Amp circuit breaker or for the 120V 500VA 1-phase control transformer?
For grounding purposes there is a #2 GA grounding lug at the panel grounding bar - sized for the 500Amp circuit breaker .
The panel enlosure itself is supplied with (3) grounding stud connection points for (2) grounding wires.
One grounding wire is attached from a stud on the inner wall of the enclosure to the enclosure door and (1) wire is attached from the same stud at the inner wall of the enclosure to the removeable inner panel.
For the (2) grounding wires that connect the enclosure to the door and to the inner panel - what wire size is needed?
Are these (2) "enclosure/door/panel" grounding wires sized for the 500Amp circuit breaker or for the 120V 500VA 1-phase control transformer?