Hendrix
Senior Member
- Location
- New England
If one is to replace a non grounded receptacle with a GFCI receptacle, can one then replace the two wire receptacles on the load side of the GFCI with grounding type receptacles?
406.4(D)2C. Is not saying that I don't think.Yes, as long as those load-side receptacles are replaced with GFCI receptacles.
Sent from my SM-G935P using Tapatalk
If one is to replace a non grounded receptacle with a GFCI receptacle, can one then replace the two wire receptacles on the load side of the GFCI with grounding type receptacles?
Yes, that is the way 2014 NEC 406.4(D)(2)(c) reads, BUT that is not the only thing it says . . . those GFCI LOAD-side replacement grounding-type receptacles must be labeled as described and they cannot be connected to an EGC.If one is to replace a non grounded receptacle with a GFCI receptacle, can one then replace the two wire receptacles on the load side of the GFCI with grounding type receptacles?
Yes , they also need to be marked no equipment ground and GFCI protected.
Good. That side steps a more complicated discussion about 406.4(D)(1) with respect to armored cable or flexible metallic conduit.It's NMC
:happyyes:
You may also need AFCI protection depending on state/code cycle.
Yes!To the OP: if you want to do the 406.4 gfci exception noted above and afci protection is required per your cycle, but the panel is of a vintage for which afci/gfci breakers are not available- you can simply install a AFCI/GFCI (DFCI) receptacle and feed the labeled grounding type recs off of that.