If I install a gfci up stream from a two wire receptacle and install a three wire receptacle ( no egc ) and mark the receptacle with gfci protected no egc what can and cant I plug in to that ?
The way I read 250.114 you cant use anything with a three wire ( plug with egc ) cord no a three wire receptacle with no egc ?
What advantage would it be to install a gfci up stream of a three wire receptacle with on egc over installing two wire receptacles ?
What advantage would it be to install a gfci up stream of a three wire receptacle with on egc over installing two wire receptacles ?
Ability to install grounded receptacles.
My question is by the NEC what good is a three wire receptacle with no egc on a up stream gfci if by the nec you cant use a three wire plug in it I know it provides gfci protection I also people will use it as a with three wire plug .
If I install a gfci up stream from a two wire receptacle and install a three wire receptacle ( no egc ) and mark the receptacle with gfci protected no egc what can and cant I plug in to that ?
Simple last question is their anything with a three wire cord I can plug in to this three wire receptacle gfci protected with no EGC by nec ?
Simple last question is their anything with a three wire cord I can plug in to this three wire receptacle gfci protected with no EGC by nec ?
Maybe...if you have something with a 3 wire cord that is not on the list in 250.114(3), you can plug it into the 3 wire receptacle that is GFCI protected and does not have an EGC run to it.yes or no ?
Maybe...if you have something with a 3 wire cord that is not on the list in 250.114(3), you can plug it into the 3 wire receptacle that is GFCI protected and does not have an EGC run to it.
What is the problem with using certain appliances on a GFCI w/no EGC? a GFCI doesnt need a ground to function properly, so why the restrictions on what you can plug into one w/o one?
What is the problem with using certain appliances on a GFCI w/no EGC? a GFCI doesnt need a ground to function properly, so why the restrictions on what you can plug into one w/o one?
I think it may be because GFCIs do not always prevent a shock, they just limit how long you get it
Think of a refrigerator with no EGC, it ground faults but it is sitting on plastic wheels on a hardwood floor so there is no current flow, it sits there live maybe for a long time.
Now one day you happen to touch the fridge and the sink at the same time, ZAPP! You will get blasted until the current through your body rises to 6 ma or so and the GFCI opens. This all takes time.
If I remember correctly the member here zog got hung up on 120 messing with a pump in a pond or something until a GFCI tripped. He said it seemed long and painful.
Time basically stops when you are getting shocked.
What article lists what appliances cant be used unless an EGC is present?