SMB Member Location North Charleston, SC Apr 1, 2010 #1 Is it a code violation to connect two conductors under one CB terminal? I have two #12 under one 20/1 CB.
Is it a code violation to connect two conductors under one CB terminal? I have two #12 under one 20/1 CB.
V Volta Senior Member Location Columbus, Ohio Apr 1, 2010 #2 Unless it is identified for more than one, yes. This thread is a poll on peoples opinions on how dangerous it is. It can vary greatly, IMO.
Unless it is identified for more than one, yes. This thread is a poll on peoples opinions on how dangerous it is. It can vary greatly, IMO.
roger Moderator Staff member Location Fl Occupation Retired Electrician Apr 1, 2010 #3 SMB said: Is it a code violation to connect two conductors under one CB terminal? I have two #12 under one 20/1 CB. Click to expand... See the last sentence 110.14(A) and then research the manufacturers info for the particular breaker. Roger
SMB said: Is it a code violation to connect two conductors under one CB terminal? I have two #12 under one 20/1 CB. Click to expand... See the last sentence 110.14(A) and then research the manufacturers info for the particular breaker. Roger