jbowman88
Member
- Location
- Renton, WA
If installing a listed Type 1 SPD on the load side of the service disconnect (as a Type 2 ), is the SPD required to have a separate OCPD?
I’m installing a new service disconnect with breaker on the exterior of a building (480Y/277), which then goes through a tap box to an MDP. There will be a sub-meter that connects inside the tap box (no utility meter, primary metered campus). I would like to also put the SPD right next to the tap box, and tie it into the lugs inside, but not sure if I can do that without OCPD, even with the Type 1 SPD…
Maybe somebody can explain to me the advantage of installing an SPD on the line side of the service disconnect? It just makes it a PITA to work on down the road. Also, I’ve seen few (no?) disconnects that have additional lugs or a means to connect the SPD on the line side. How are folks accomplishing this?
Thanks
I’m installing a new service disconnect with breaker on the exterior of a building (480Y/277), which then goes through a tap box to an MDP. There will be a sub-meter that connects inside the tap box (no utility meter, primary metered campus). I would like to also put the SPD right next to the tap box, and tie it into the lugs inside, but not sure if I can do that without OCPD, even with the Type 1 SPD…
Maybe somebody can explain to me the advantage of installing an SPD on the line side of the service disconnect? It just makes it a PITA to work on down the road. Also, I’ve seen few (no?) disconnects that have additional lugs or a means to connect the SPD on the line side. How are folks accomplishing this?
Thanks