Would a type 1 TVSS be permitted to be tapped off a main lug switch board prior to any of the main breakers as in article 285.23 or would i have to follow 285.24 rules.
The main lug switch board is located indoors and is fed from outdoor under ground secondary transformer conductors.( Feeder Conductors)
Rick
285.23 Type 1 SPDs (Surge Arresters).
Type 1 SPDs shall be installed in accordance with 285.23(A) and (B).
(A) Installation. Type 1 SPDs (surge arresters) shall be installed as follows:
(1) Type 1 SPDs (surge arresters) shall be permitted to be connected to the supply side of the service disconnect as permitted in 230.82(4) or
(2) Type 1 SPDs (surge arresters) shall be permitted to be connected as specified in 285.24.
285.24 Type 2 SPDs (TVSSs).
Type 2 SPDs (TVSSs) shall be installed in accordance with 285.24(A) through (C).
(A) Service-Supplied Building or Structure. Type 2 SPDs (TVSSs) shall be connected anywhere on the load side of a service disconnect overcurrent device required in 230.91, unless installed in accordance with 230.82(8).
(B) Feeder-Supplied Building or Structure. Type 2 SPDs (TVSSs) shall be connected at the building or structure anywhere on the load side of the first overcurrent device at the building or structure.
(C) Separately Derived System. The SPD (TVSS) shall be connected on the load side of the first overcurrent device in a separately derived system.
The main lug switch board is located indoors and is fed from outdoor under ground secondary transformer conductors.( Feeder Conductors)
Rick
285.23 Type 1 SPDs (Surge Arresters).
Type 1 SPDs shall be installed in accordance with 285.23(A) and (B).
(A) Installation. Type 1 SPDs (surge arresters) shall be installed as follows:
(1) Type 1 SPDs (surge arresters) shall be permitted to be connected to the supply side of the service disconnect as permitted in 230.82(4) or
(2) Type 1 SPDs (surge arresters) shall be permitted to be connected as specified in 285.24.
285.24 Type 2 SPDs (TVSSs).
Type 2 SPDs (TVSSs) shall be installed in accordance with 285.24(A) through (C).
(A) Service-Supplied Building or Structure. Type 2 SPDs (TVSSs) shall be connected anywhere on the load side of a service disconnect overcurrent device required in 230.91, unless installed in accordance with 230.82(8).
(B) Feeder-Supplied Building or Structure. Type 2 SPDs (TVSSs) shall be connected at the building or structure anywhere on the load side of the first overcurrent device at the building or structure.
(C) Separately Derived System. The SPD (TVSS) shall be connected on the load side of the first overcurrent device in a separately derived system.