....is the bonding strip actually doing anything ?
I recall a recent thread about what to do with the bond (cut, fold, wrap, etc)....the post linked to an "information sheet" (pdf?) can someone post that again?
Here's the story....unit is being roughed in (all type AC), as the guys are cutting in the boxes someone notices that there is no bonding strip in the cable ??? Back tracking a few locations, there is still no strip...wtf?...Maybe an entire roll?
Looking in the NEC [2002]:
So, what say you?
I recall a recent thread about what to do with the bond (cut, fold, wrap, etc)....the post linked to an "information sheet" (pdf?) can someone post that again?
Here's the story....unit is being roughed in (all type AC), as the guys are cutting in the boxes someone notices that there is no bonding strip in the cable ??? Back tracking a few locations, there is still no strip...wtf?...Maybe an entire roll?
Looking in the NEC [2002]:
NECH [2002] goes on to indicate:320.100 Construction.
Type AC cable shall have an armor of flexible metal tape and shall have an internal bonding strip of copper or aluminum in intimate contact with the armor for its entire length.
It appears to me (and I seem to be batting .000 lately) that the strip is not doing much of anything (see bolded text above)...but with my average - that's gotta be wrong!
The armor of Type AC cable is recognized as an equipment grounding conductor by 250.118. The required internal bonding strip can be simply cut off at the termination of the armored cable, or it can be bent back on the armor. It is not necessary to connect it to an equipment grounding terminal. It reduces the inductive reactance of the spiral armor and increases the armor's effectiveness as an equipment ground. Many installers use this strip to help prevent the insulating bushing required by 320.40 (the ?red head?) from falling out during rough wiring.
So, what say you?