Re: Type "D", thermo-magnetic breaker??
Thanks for the reply. I am always learning new info. from you guys. I think you are right. It seems he is talking about miniature breaker with type D trip curve. But I don't think he knows the difference between UL 489 & UL1077.
What is the load you are planning on protecting?
Ron,
My load is a "Ultra Violet System" on Swimming pool. 480V, 3Ph, 60Hz, 5Kw. They are asking for a 32Amp rating, Type "D" thermo-magnetic internal circuit breaker as well as external.
I think I can give them a miniature breaker with D trip curve for internal cb comply with UL1077 but the external cb wil have to be UL489 complied for brach circut protection.
Then my next question is
1) Can I use this miniature cb with typical molded circuit breaker, like HACR type? (MCCB trip at about 5-10x of the rating and type D trips at 10-14x. MCCB will always trip first before type D).
or should I use high magnetic withstand cb like ron suggested?
2) How does this slow trip cb protect the sensitive load?
3) Ron, when you use this "high magnetic withstand cb", do you always perform the selective coordination?
Thanks.