I've seen conflicting opinions on where or not type NM cable, when used to feed an AC unit covered under article 440, that it is required to be sized at 60 degrees Celsius? 334.80 states: 'The ampacity shall be in accordance with the 60 degree Celsius conductor rating'. I see no exception for conductors feeding AC units so I'm assuming that if I use Romex to feed an AC unit I can only use the 60 degree ampacity. Any comments?