charlie
Senior Member
- Location
- Indianapolis
Section 334.15(C) now states, "NM cable used on a wall of an unfinished basement shall be permitted to be installed in a listed conduit or tubing. conduit or tubing shall utilize a nonmetallic bushing or adaptor at the point where the cable enters the raceway. Metal conduit and tubings and metal outlet boxes shall be grounded."
Since the NM cable can not be secured within 12" of the outlet box, 334.30 has a sentence that states, "Sections of cable protected from physical damage by raceway shall not be required to be secured within the raceway."
I was going to question the argument that it is now permitted to use a short run of EMT down a basement wall to a handy box but I found the rest of the change in section 334.30. For years, this has been done and has not met the technical requirements of the Code; however, with these two changes, it will be acceptable when the 2005 NEC is adopted (just don't forget the raceway fill restrictions).
Since the NM cable can not be secured within 12" of the outlet box, 334.30 has a sentence that states, "Sections of cable protected from physical damage by raceway shall not be required to be secured within the raceway."
I was going to question the argument that it is now permitted to use a short run of EMT down a basement wall to a handy box but I found the rest of the change in section 334.30. For years, this has been done and has not met the technical requirements of the Code; however, with these two changes, it will be acceptable when the 2005 NEC is adopted (just don't forget the raceway fill restrictions).