Type tc cable for panel feeder

Status
Not open for further replies.

drwill

Member
Does anyone see any problem with running type TC cable from the service panel to a sub panel in a garage.(this is for a house)the reason why is that its almost half the cost of SER


Thanks Will D
 
Re: Type tc cable for panel feeder

Section 336.2 of the 2002 NEC appears to indicate Type TC cable is only to be "installed in cable trays, in raceways, or where supported by a messenger wire."

I'm not exactly sure if tray cable has the same fire-propagation and smoke-release characteristics of NM and SE cable.

Cost should not be your primary concern. I would consult your local AHJ.
 