weressl said:
When you install a NEMA 4 box what kind of connections are allowed to be made to it. Doesn't the connections need to maintain the NEMA rating of said box?
If you install a NEMA 4 box and you require a connection to a NEMA 1 box, wouldn't the interconnecting item would need to maintain the higher rating?
Wouldn't you secure the cable at the point of entry?
When you leave the conduit open don't you allow free contaminants, including water to freely enter?
Matter of fact we have found waterfull of motor pecker-heads as the result of this type installation. In MCC's where a single ~2' vertical conduit with pop-on bushing was utilized to 'drop-in' several cables allowed the free passage of dust to enter and accumulate in the MCC eventually resulting in dust carbonization, tracking and overflash.
As I said if you leave both end of the conduit open and make proper cable termination into the target device, I see no problem.
I'm not quite sure what you are refering to as "pop on bushings", but in response to your other questions,
The ty rap with base I was talking about earlier should provide adequate support for the cable where it enters the enclosure and duct sealing around the ground bushing where the cable enters the coduit should prevent contaminents from entering the jbox. (It does because we've done it in other industrial facilities and duct seal work fine).
I'm not against using cgb's on a coupling at the end of my conduit, but would prefer ductseal or some other sealing method. This would allow installing more than one cable in a nipple, which with a large number of small cables is nice.
Dux seal is no different than duct tape, with the exception that duct tape IS developed and approved to seal minute air-leaks in a crimped sheet-metal duct-work.
Dux seal compound is a temporary repair, fix in my book I would never use it for permanent installation. On the other hand my industry maybe subject to much harsher conditions than others. I just know what works and what isn't. Although it is resistant to shrinking it is not immune to it. Let me know if you intend to have a maintenance program going along with that to check for leaky patches.:grin:
As the profit pressures grow and the available workforce shrinks our primary objective is to minimize installations that require attention. Usually complex machinery, switchgear and control systems are much more complex and requiring higher skill so I wouldn't want to insult our skileld technicians to look for leaky seals.
I like to specify and use devices that are designed for the specific purpose, and select the best design for that specific use and refrain from inventive 'other uses'. I believe for example that the best multicoinductor sealing product is made by Roxtec.
http://www.roxtec.com/ Even though it is an offshore product, it is superior in performance and flexibility to the other US made ones.