Please check my work:
Usually the utility provides service laterals but this is a non-residential project (dairy, office, and retail sales), so I would need to provide it. As non-residential Table 310.15(B)(6) does not apply.
So according to Table 310.16 (USE) it is:
75 degree column...600 kcmil copper or 900 kcmil aluminum.
90 degree column...500 kcmil copper or 700 kcmil aluminum.
...and the 75 degree column applies because of the termination at the meter pedestal?
Usually the utility provides service laterals but this is a non-residential project (dairy, office, and retail sales), so I would need to provide it. As non-residential Table 310.15(B)(6) does not apply.
So according to Table 310.16 (USE) it is:
75 degree column...600 kcmil copper or 900 kcmil aluminum.
90 degree column...500 kcmil copper or 700 kcmil aluminum.
...and the 75 degree column applies because of the termination at the meter pedestal?