Type USE2 wire in conduit?

Status
Not open for further replies.

northern

Member
Location
Vermont
Wiring a solar PV array, the strings need to get into a building to a combiner box, Can single conductor use2 cable be run from the pv panels into a weatherhead and through a short conduit run (6'or less) to the combiner box?
 

bennie

Esteemed Member
Re: Type USE2 wire in conduit?

USE cable is not restricted for only underground service entrance use.(weird sentence) ;)

There is another identification mark to indicate the insulation and temperature rating. This mark will indicate the approved application.
 

northern

Member
Location
Vermont
Re: Type USE2 wire in conduit?

That answers my question, thanks Bennie. The cable has multiple ratings including RHH RHW, so it would be fine for conduit. I quess I was confused because USE wire normally is only allowed to go 6 feet into a building, I think because it is not fire/smoke rated. - back to work..
 