type W cable acceptable usages

Status
Not open for further replies.

bradb

Member
We recently upgraded an Imax theatre projection system to 3-D. The projectors move on transporters. The Imax specs required 2/0 welding cable(type W). The projectors are powered by DC output from rectifiers. Our inspector failed us claiming that welding cable cannot be used as fixed wiring. Can you help justify type W cable or recommend another?
 

earlydean

Senior Member
Re: type W cable acceptable usages

Type "W" portable power cable is found in Table 400.4. Article 400.7(A)(10) allows the use of cords and cables for moving parts.
 

tom baker

First Chief Moderator & NEC Expert
Staff member
Location
Bremerton, Washington
Occupation
Master Electrician
Re: type W cable acceptable usages

Type W and Welding cable are not the same. Welding cable is not a listed power cable, Type W is.
 