J Jeff Rae Member May 30, 2006 #1 can you run U.F. cable inside PVC conduit if not what artical address this if so must you derate the wire????
can you run U.F. cable inside PVC conduit if not what artical address this if so must you derate the wire????
B bphgravity Senior Member Location Florida May 30, 2006 #2 Yes, type UF is permitted in RNC per 352.22 of the 2005 NEC. "Derating" is only required if a correction or adjustment factor applies per 310.15
Yes, type UF is permitted in RNC per 352.22 of the 2005 NEC. "Derating" is only required if a correction or adjustment factor applies per 310.15
Pierre C Belarge Senior Member Location Westchester County, New York May 30, 2006 #3 If you are following the 2005 NEC the answer is yes you can. look in 352 and 340.