hhsting
Senior Member
- Location
- Glen bunie, md, us
- Occupation
- Junior plan reviewer
I have apartment complex dwelling unit where condensing unit in outdoor balcony is being replaced. They are using UF cable from dwelling unit panelboard for branch circuit.
The note says the following:
Provide new branch circuit in conduit from the panelboard thru attic to new condensing unit. Wiring outside exposed to weather shall be routed in metallic conduit with weather resistant coating with AHJ approval UL wire maybe used. Protect UF cable in accordance with NEC 2014.
Only part confusing is when UF cable is outside it says to route in metallic conduit with weather resistant coating. Is this allowable for UF cable? I looked at 340.10(4) which refers to 334 NM cable but 334.15(B) says only use EMT, RMC, IMC.
The note says the following:
Provide new branch circuit in conduit from the panelboard thru attic to new condensing unit. Wiring outside exposed to weather shall be routed in metallic conduit with weather resistant coating with AHJ approval UL wire maybe used. Protect UF cable in accordance with NEC 2014.
Only part confusing is when UF cable is outside it says to route in metallic conduit with weather resistant coating. Is this allowable for UF cable? I looked at 340.10(4) which refers to 334 NM cable but 334.15(B) says only use EMT, RMC, IMC.