Can uf cable be used for outdoor commercial wiring,specifically an outdoor dining area,inside is PA outside about 30 people.
UF can be used outdoors if it is protected as long as the building qualifies under 334.10
340.12 Uses Not Permitted.
Type UF cable shall not be used as follows:
(1) As service-entrance cable
(2) In commercial garages
(3) In theaters and similar locations
(4) In motion picture studios
(5) In storage battery rooms
(6) In hoistways or on elevators or escalators
(7) In any hazardous (classified) location, except as otherwise permitted in this Code
(8) Embedded in poured cement, concrete, or aggregate, except where embedded in plaster as nonheating leads where permitted in 424.43
(9) Where exposed to direct rays of the sun, unless identified as sunlight resistant
(10) Where subject to physical damage
(11) As overhead cable, except where installed as messenger-supported wiring in accordance with Part II of Article 396
I assumed the outdoor dinning was attached to the structure so I thought it would still apply.