UF depth of burial

Status
Not open for further replies.

Bobhook149

Senior Member
using table 300.5 column 4 does this mean you can use UF if it is GFCI protected and 120v in a residence at a depth of 12''??
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
using table 300.5 column 4 does this mean you can use UF if it is GFCI protected and 120v in a residence at a depth of 12''??
I agree with the others, however if this is a common area to some townhouses or condos, then this rule should not apply. If it is strictly for a residence then I totally agree.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
one & two family dwellings, yes. beyond that, you need to watch for drives & parking.
 