Is uf 12-3 allowed to be installed in pvc for a pool pump if the bare insulated conductor is not used and the red is taped green.


I dont see in the code where it says you cant.
 

fireryan

Senior Member
Location
Minnesota
I believe 250.119 says that the egc must have a continous outer finish that is either green or green with one or more yellow stripes or bare
 

JohnJ0906

Senior Member
Location
Baltimore, MD
Is uf 12-3 allowed to be installed in pvc for a pool pump if the bare insulated conductor is not used and the red is taped green.


I dont see in the code where it says you cant.

250.119(B).

I don't think that this would meet the requirement in the 1st half of the sentence.
What will ensure that only qualified persons service the installation?
 

cpal

Senior Member
Location
MA
You not allowed to re-identify a grounded conductor 6 or smaller. I believe the Code is silent on phase identification
 