Ufer and Ground Rods

Merry Christmas

Kenkamba

Member
Location
Culver City
Occupation
Electrical Contractor
IF the code only requires an Uffer ground or if not possible then ground rods at the main service, then why do electrical engineer's show both Uffer and ground rods on their single line for a new construction single-family residence?
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
In our area the utility requires a rod on all meter enclosures regardless of any other electrodes present. It's possible that may apply in your area
 

rc/retired

Senior Member
Location
Bellvue, Colorado
Occupation
Master Electrician/Inspector retired
IF the code only requires an Uffer ground or if not possible then ground rods at the main service, then why do electrical engineer's show both Uffer and ground rods on their single line for a new construction single-family residence?
The code does not require a Ufer, concrete encased electrode.
Cookie cutter plans
As Mr. Baker stated, lack of knowledge.

Ron
 

Elect117

Senior Member
Location
California
Occupation
Engineer E.E. P.E.
In California it could be due to the increased use of vapor barriers. I have been in discussions where their use was left off of the plans for the electrical and when the contractor showed up they expected to be able to use the concrete encased electrode + building steel for the dry types in the building.

It ended up being a simple fix to go to the cold water, but there was an issue of who screwed up and who was responsible for the cost to make that correction and blah blah blah.

I imagine it is the same (minus the dry types) for residential.

It is a catch all for if there is a vapor barrier, plastic water piping, etc. That way there is no argument on who messed up and who is paying to make the fix on material, etc.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
IF the code only requires an Uffer ground or if not possible then ground rods at the main service, then why do electrical engineer's show both Uffer and ground rods on their single line for a new construction single-family residence?
Ignorance or as Tom suggested using both electrodes makes them feel warm and fuzzy. The CEE is only required when the rebar meets the 1/2" or larger and 20' or longer minimum. Since the CEE does not require a supplemental electrode it can stand alone as the sole electrode making up the GES.
 

Murphy79

Member
Location
Kansas City , MO
Occupation
Master Electrician/ Elelectrical Contractor/Instructor/ Solar
IF the code only requires an Uffer ground or if not possible then ground rods at the main service, then why do electrical engineer's show both Uffer and ground rods on their single line for a new construction single-family residence?
They may be giving you options or sometimes you may want to do both and that way you'll have supplemental grounding as required by some jurisdictions. This will ensure that some type of grounding is in place in just case loose one of them for some strange reason.
 

jaggedben

Senior Member
Location
Northern California
Occupation
Solar and Energy Storage Installer
... loose one of them for some strange reason.