Couple of questions:
1) I always use a ufer ground for my GEC. By virtue of that fact, I do not run a seperate building steel bonding conductor since the steel in the footing which the Ufer is tied to will generally tie into a column pier or grade beam and pick up building steel through a base plate. Am I wrong in this?
2) Having a debate with my field supervisor. He maintains that a cold water bond needs to be connected within 5 feet of the water system's entry into the building. I feel that since we routinely use a Ufer as GEC, and the 5 foot rule applies to using the cold water piping as a GEC, the cold water bond can be made at any accessible location in the piping system.
Any input is appreciated.
1) I always use a ufer ground for my GEC. By virtue of that fact, I do not run a seperate building steel bonding conductor since the steel in the footing which the Ufer is tied to will generally tie into a column pier or grade beam and pick up building steel through a base plate. Am I wrong in this?
2) Having a debate with my field supervisor. He maintains that a cold water bond needs to be connected within 5 feet of the water system's entry into the building. I feel that since we routinely use a Ufer as GEC, and the 5 foot rule applies to using the cold water piping as a GEC, the cold water bond can be made at any accessible location in the piping system.