On a jobsite where conflicting information is being thrown around (I'm sure many of you are familiar) and it has me doubting myself.
Couple questions...
1) Does a ground rod have to be a minimum of 6' away from the ufer ground?
2) Does the ground rod and ufer need to be bonded together before connecting into the panelboard? When the code says they must all be bonded together does that include the neutral/ground bus in the panel or no?
3) The new structure being built is going to store paint. I have read that in NFPA 780 it requires the ground rods to be apart the same distance as length of the rods to help with lightning dispersion for places with volatile liquids. However, I don't have a copy of the 780 and we typically go off NFPA 70 (which states no less than 6' apart) so what should be my thinking on this?
Couple questions...
1) Does a ground rod have to be a minimum of 6' away from the ufer ground?
2) Does the ground rod and ufer need to be bonded together before connecting into the panelboard? When the code says they must all be bonded together does that include the neutral/ground bus in the panel or no?
3) The new structure being built is going to store paint. I have read that in NFPA 780 it requires the ground rods to be apart the same distance as length of the rods to help with lightning dispersion for places with volatile liquids. However, I don't have a copy of the 780 and we typically go off NFPA 70 (which states no less than 6' apart) so what should be my thinking on this?