Ufer Ground- 20 ft of continuous rebar?

Status
Not open for further replies.

Electron_Sam78

Senior Member
Location
Palm Bay, FL
For a ufer (CEE) the NEC says at least 20 ft of 1/2" rebar. Does that mean on continous, solid 20 ft section or can sections be tied together with the normal ties to make up the 20 ft?
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
CA, does a building require Ufer grounding or is a ground rod suitable?

Unless CA has an amendment then a ufer is required for new construction as of 2008 ( it was req. in 2005 but is now clarified). The rods would be fine for service upgrades etc.
 