Yes, as has been pointed out. Just make sure the bonding jumpers are sized accordingly. For example, if you're permitted to use a #6 cu GEC to the rebar and then you go to the water which requires, say, #4, you'll be in violation because the water pipe bonding jumper would be reduced to an unacceptable size. :smile:
Only the part that that connects only a rod/plate electrode.under what conditions could the size of the bonding jumpers be reduced?
How would you non-reversibly connect to a water pipe?our local AHJ likes to all be connected together with weld or non reversable (compression sleeve)
The size of the GEC is determined by what you are connecting it to, based on 250.66, IE a CEE only requires a 4 AWG max.under what conditions could the size of the bonding jumpers be reduced (i.e from water line to ufer, or to rebar or to structural) ? also noted in the picture that mechanical clamps are used on water line, and continuing to another electrode. our local AHJ likes to all be connected together with weld or non reversable (compression sleeve)
also noted in the picture that mechanical clamps are used on water line, and continuing to another electrode. our local AHJ likes to all be connected together with weld or non reversable (compression sleeve)