What I have done to save money on a ufer ground is stub up a piece or rebar underneath were the panel is going to go. I then also stub up a piece of rebar 25 feet away for a reference if the inspector wants to check the resistance. Then I put a acorn with #4 on the rebar with a 2 gang mud ring for access and call it good.
Washington administrative code or (WAC) says they need to be less than 25 ohms or resistance. Or so an inspector told me. One inspector actually made me leave him wire so he could test it?
Well, first you have to also provide him another ground with less than 1 ohm resistance to use as a reference.Really, local code very interesting. How exactly would they test it?
Washington administrative code or (WAC) says they need to be less than 25 ohms or resistance. Or so an inspector told me. One inspector actually made me leave him wire so he could test it?
In another thread the OP described an area where the inspector would not look at the connection and rebar pre-pour but required two wires to be brought out at least 20' apart so all he had to do was check continuity between them.I think his point was he wanted to check the resistance to make sure that the rebar was continuous for that length.
I think his point was he wanted to check the resistance to make sure that the rebar was continuous for that length.
I thought of commenting earlier that this may just be to do a simple check for continuity between the two points. The next question that would bring up is what kind of reading is considered go/no go? A NEC compliant CEE could be multiple pieces of rebar in concrete connected together only by tie wires. In that kind of instance I would expect continuity but not necessarily extremely low resistance like you would get if you had both ends of a single 25 foot piece of rebar stubbed out of the footing.In another thread the OP described an area where the inspector would not look at the connection and rebar pre-pour but required two wires to be brought out at least 20' apart so all he had to do was check continuity between them.
Seems logical it would be, but go to a pretty dry location, a new footing probably is low resistance as there is still moisture in the fresh concrete, but one that has been there for some time may not be quite as low resistance, though that kind of gets off track of an inspection of a new CEE anyway.I would hope less than one ohm.