Re: Ufer ground
Originally posted by volt102:
Why not just put 20' of copper in the footing. You need to use the concrete encased electrode because you have rebar in the footing. If you put the 20' of copper in the concrete it would satisfy 250.52(A)(3) wouldn't it?
Jim
I think that maybe Jim is on to something here.
If we look closely at 250.50 we see;
All grounding electrodes as described in 250.52(A)(1) through (A)(6) that are present at each building or structure served shall be bonded together to form the grounding electrode system.
Here it tells us that all electrodes in (A) 1 through 6 must be bonded together. Well I now ask what is a concrete encased electrode? In (A) 3 it states;
consisting of at least 6.0 m (20 ft) of one or more bare or zinc galvanized or other electrically conductive coated steel reinforcing bars or rods of not less than 13 mm (? in.) in diameter,
OR consisting of at least 6.0 m (20 ft) of bare copper conductor not smaller than 4 AWG.
The way I see this is if there is no rebar present then 20 foot of #4 copper will work as the electrode.
With the same breath I say that if both are present I only have to choose one of them not both.
The word OR is a word that gives choice it does not mean both or AND nor INSTEAD OF.
I see 250.52 (A) (3) as giving a choice between the rebar
OR #4 copper. I see nothing that mandates that the rebar has to be used if both are present.
(A) (3) is ?Concrete-Encased Electrode? not concrete encased rebar.