I had a over ambitious aprenttice, today decided to cut the end of a ufa ground, is it legal to do that per NEC.
"ufa ground"???
Did you mean ufer ground? In NEC terminology, it is a concrete-encased electrode, or CEE for short.
Typo or not, I'm not getting a full picture in my mind. Describe exactly what the apprentice cut—using NEC terminology—and where?
He can start chipping away the concrete any time now... :happyyes:He cut the ufer ground as it comes out of the foundation below the panel, because the panel set low,he cut about 4 inches off.
He cut the ufer ground as it comes out of the foundation below the panel, because the panel set low,he cut about 4 inches off.
He cut the ufer ground as it comes out of the foundation below the panel, because the panel set low,he cut about 4 inches off.
Is there still enough left to get a connection on? If yes, connect and move on.
250.68(C)(3) A concrete-encased electrode of either the conductortype, reinforcing rod or bar installed in accordance with
250.52(A)(3) extended from its location within the concrete
to an accessible location above the concrete shall
be permitted.
2017 NEC 250.68(C)(3) said:A rebar-type concrete-encased electrode installed in accordance with 250.52(A)(3) with an additional rebar section extended from its location within the concrete to an accessible location that is not subject to corrosion shall be permitted for connection of grounding electrode conductors and bonding jumpers. The rebar extension shall not be exposed to contact with the earth without corrosion protection.
He can start chipping away the concrete any time now... :happyyes:
Are you talking about a piece of rebar stubbed up? Regardless of whether it's a wire or rebar why do you think there's a minimum length for accessing it?He cut the ufer ground as it comes out of the foundation below the panel, because the panel set low,he cut about 4 inches off.