Question #2: Does it require a supplement? No. You must use all available electrodes, but if the concrete encased is the only one available, then nothing else can be required, unless you have a local, legally adopted law that says otherwise.Formal Interpretation 78-4
Reference: Article 250.50
Question: Is it the intent of 250.50 that reinforcing steel, if used in a building footing, must be made available for grounding?
Answer: No.
Issue Edition: 1978
Reference: 250-81
Issue Date: March 1980
Do we have to use "all available" electrodes, or not? A ufer grd is certainly available during new construction. Same as building steel, water pipe...You must use all available electrodes, but if the concrete encased is the only one available, then nothing else can be required, unless you have a local, legally adopted law that says otherwise.
For very practical reasons, NFPA does all it can to avoid Formal Interpretations. It would overwork many of the Technical Committees (TC) which are made up entirely of volunteers. Each CMP is considered to be a TC. Staff will usually issue an "informal interpretation" that about 90% of the time is adequate.6-6 Action Following Issuance of Formal Interpretation. Any TC whose Document has been the subject of a Formal Interpretation shall prepare a committee proposal clarifying the text of the Document involved. The TC shall process such a proposal in conformance with procedures set forth in 4-3. After issuance of the next edition of the document, the Interpretation shall be retired.
250.52(3) Concrete-Encased Electrode. An electrode encased by at least 50 mm (2 in.) of concrete, located within and near the bottom of a concrete foundation or footing that is in direct contact with the earth , consisting of at least 6.0 m (20 ft) of on