Ufer Ground

Status
Not open for further replies.

herkyfred

Member
Big debate here. First, is it the intent of the NEC to mandate using a Ufer ground if available? If not, by what authority? One of the NFPA subcommittees? Second, can a Ufer ground stand on it's own; i.e. does a Ufer ground require a secondary electrode?
 
Re: Ufer Ground

When i was wiring homes in Naples FL. That was the only ground they would except.Had a battle at one house cause there was none available and they refused to take 2 ground rods
 
Re: Ufer Ground

Formal Interpretation 78-4
Reference: Article 250.50
Question: Is it the intent of 250.50 that reinforcing steel, if used in a building footing, must be made available for grounding?
Answer: No.
Issue Edition: 1978
Reference: 250-81
Issue Date: March 1980
Question #2: Does it require a supplement? No. You must use all available electrodes, but if the concrete encased is the only one available, then nothing else can be required, unless you have a local, legally adopted law that says otherwise. :) Hope this helps
 
Re: Ufer Ground

I think a better question for formal interpretation would have been-
"Is it the intent to require a concrete encased electrode be installed whenever a building is constructed with concrete footings?"

The question asked above just asks about using the rebar already in the footing. We get a seperate piece of rebar or copper used for the UFER. The seperate rebar has been that way forever and I don't know how that came about.

Do other places use the structural rebar for the UFER

Since the footing is open for inspection of the steel, we feel that a concrete encased electrode is available and by that we require it to be installed.

btw - Ryan, do you have a link or something you could share on where formal interpretations are available
Thank You
 
Re: Ufer Ground

I have read some discussions and a few IEEE reports on suplementing concrete-encased electrodes on the basis of lightning ssues and not resistance reduction.

It is believed that direct lightning strikes to concrete-encased systems are likely to damage/crack the foundation of a building, whereas adding a supplement ground rod helps to defer some of the strike intensity away from the slab.

Lightning is a wild event and is really the only strong basis for having a grounding electrode system, other than other high-voltage crossover events.
 
Re: Ufer Ground

Larry: I actually got that out of the handbook, section 250.50. I just happened to know that formal interpretation was right there. I think there are links on NFPA's website if you are a member...I'll look into it :)
 
Re: Ufer Ground

I've tried looking there, but did not see anything that jumped out at me. Also tried the search engine in the NFPA site, but no help.
Maybe you'll have better luck
 
Re: Ufer Ground

I did too Larry, but didn't have any luck either.

It would sure be nice if a person could get his or her hands on a list of formal interpretations. Maybe even make a book of them??? :cool:
 
Re: Ufer Ground

You must use all available electrodes, but if the concrete encased is the only one available, then nothing else can be required, unless you have a local, legally adopted law that says otherwise.
Do we have to use "all available" electrodes, or not? A ufer grd is certainly available during new construction. Same as building steel, water pipe...

This question has been asked before, with the answer being only one electrode is required.

Brent
 
Re: Ufer Ground

This is a list of all current Formal Interpretations that have not otherwise been "clarified" in the body of current text.

NEC Formal Interpretations

For some of you these are in the back of your NEC as well.

Of interest to this discussion as well, check this and scroll down to CMP5's "clarification." It only took 27 years :D

CMP Chairman Reports

[ July 08, 2004, 09:35 PM: Message edited by: rbalex ]
 
Re: Ufer Ground

Thanks for the links and the insight that interpretations are "deleted" after clarified in the text of the Code.

Wow only three interpretations left, I thought with such a widley discussed document there would've been more.
 
Re: Ufer Ground

You may find some interest in this too:

REGULATIONS GOVERNING COMMITTEE PROJECTS

Section 6 outlines the entire Formal Interpretation process.

This is why I "chuckled" at the 27 year delay:

6-6 Action Following Issuance of Formal Interpretation. Any TC whose Document has been the subject of a Formal Interpretation shall prepare a committee proposal clarifying the text of the Document involved. The TC shall process such a proposal in conformance with procedures set forth in 4-3. After issuance of the next edition of the document, the Interpretation shall be retired.
For very practical reasons, NFPA does all it can to avoid Formal Interpretations. It would overwork many of the Technical Committees (TC) which are made up entirely of volunteers. Each CMP is considered to be a TC. Staff will usually issue an "informal interpretation" that about 90% of the time is adequate.
 
Re: Ufer Ground

I have been on CMP-10 since 1993 and have never had a formal interpretation since that time.

As far as the Ufer is concerned, I believe (I have not researched it) if reinforcing steel is used in a building footing, it will be required to be used for a grounding electrode. That will eliminate ground rods if footer steel is present. :D
 
Re: Ufer Ground

I guess that shows how good NFPA staff is a fending them off :D

I don't have the figures in front of me at the moment but I believe less than a dozen NEC Formal Interpretations have been processed in the last 30 years.

I have served on four NFPA TCs and processed a few TIA's but no FI's.
 
Re: Ufer Ground

We use UFER alone as the ground on a service.But I see a problem with it.Since here we use slabs that are encased in plastic,where is the earth contact ??? This has come up several times with AHJ and as I write this there is supposed to be an addopted addendum being written that requires ground rod(s) in addition to the UFER.
 
Re: Ufer Ground

a.wayne,
If the concrete is not in direct contact with the earth, it is not an electrode. See 250.52(A)(3).
Don
 
Re: Ufer Ground

i agree but the building dept requires the slab to be encased in plastic sheeting.That is my point how can it be earth grounded without contact ??? As long as there is a 20 ft. piece of # 5 rebar stubbed out it passes.
 
Re: Ufer Ground

250.52(3) Concrete-Encased Electrode. An electrode encased by at least 50 mm (2 in.) of concrete, located within and near the bottom of a concrete foundation or footing that is in direct contact with the earth , consisting of at least 6.0 m (20 ft) of on
 