Jim Follett
Member
- Location
- Houston, Texas
- Occupation
- Estimator / Project Manger / Designer
We have been trying to get a proper method of applying the UFER ground in new construction where there is a complete vapor barrier between the concrete slab, and earth. In these installations, the slab is not actually in contact with the earth. I have been telling our crews to install a properly sized, bare grounding conductor, at least 30' long. Connecting one end to an exposed slab rebar, then 20' away, connecting to another rebar in the same slab. The section of bare copper conductor installed between these two rebar connections, is installed below the vapor barrier, in direct contact with the earth. The remaining end of this conductor is connected to the main service ground connection. This is usually installed in the main service tap enclosure, main service wireway, or the main service OCP device. This depends on the particular service design. The AHJ's across the state require we install the UFER grounds, in all new construction. NEC 250.52 (3) "Informational Note" states "Concrete Installed with insulation, vapor barriers, films, or similar items separating the concrete from the earth is not considered to be in "direct contact" with the earth. So, essentially all we are doing here is bonding the slab back to the service ground. I don't have a problem with this installation, but want to know if anyone sees an issue with this.