Joseph Alexander
Member
When an Ufer ground is placed do you still need the supplemental ground rod? 2011- 250.53 would lead me to think that you do not.
When an Ufer ground is placed do you still need the supplemental ground rod? 2011- 250.53 would lead me to think that you do not.
Ditto same here. You could have a full ground ring, Ufer, and radials. POCO could careless because if you do not have a rod below their meter, you do not get connected. Motto here is drive two rods, call it a day, and collect a check.I have a slightly different answer: The NEC does not require a supplemental grounding electrode.
ALL of the Power Companies I work with require a ground rod at their meters.
I have a slightly different answer: The NEC does not require a supplemental grounding electrode.
ALL of the Power Companies I work with require a ground rod at their meters.
I have never seen a power company dig up to look for a rod. They see the CONCRETE ENCASED ELECTRODE wire and have no idea where it is connected to but they also don't specifically ask for rods.
Same goes for the areas we normally work.I usually install the the grounding rod near or say within a foot or two of the UFER /rebar and bond together.Is there any violation to this type install?For instance if there is no rebar/UFER present then the grounding rods are spaced 6' or greater apart form each other.ThanksI have a slightly different answer: The NEC does not require a supplemental grounding electrode.
ALL of the Power Companies I work with require a ground rod at their meters.
Same goes for the areas we normally work.I usually install the the grounding rod near or say within a foot or two of the UFER /rebar and bond together.Is there any violation to this type install?For instance if there is no rebar/UFER present then the grounding rods are spaced 6' or greater apart form each other.Thanks
Lucky guys, we are not allowed to enter the meter with the GEC in my area?..
If you already have a CEE then you do not need a ground rod. The CEE and ground rod if installed can be less than 6' apart.