Does 250.68 C 2 mean tie wire from rebar to anchor bolts for steel eliminate the requirement for a ufer? Do you always need a ufer for your grounding system?
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
It means that if you connect a GEC to the steel, you have also made a connection to the concrete encased electrode.
 

tom baker

First Chief Moderator & NEC Expert
Staff member
Location
Bremerton, Washington
Occupation
Master Electrician
Does 250.68 C 2 mean tie wire from rebar to anchor bolts for steel eliminate the requirement for a ufer? Do you always need a ufer for your grounding system?
If the rebar is present and meets the requirements for a CEE then it must be used. I have seen installations where concrete was chipped out to make the comnection
 