TinCanFury
Member
I'm looking at the thermal de-rating of cables for a 480V system that we are running in PVC conduit encased in concrete where the desire is for the top of the concrete is to be at grade and will be covered in 6" of crushed stone.
The formulas I've seen, and software like AmpCalc, both do not allow for 0" of earth above the concrete.
Table 300.5 does not address this situation. Column 3 lists nonmetallic raceways, but without concrete encasement. 300.50 addresses 600V and up, but not below. I cannot find anything that looks to reference minimum coverage for concrete encased PVC.
Is there any code requirements for conduit encased in concrete?
Does anyone know of a method for calculating thermal de-rating of cables in such a situation?
Thanks!