steveve1
- Tucson, AZ
On a large truck maintence faculity, the service entrance/distribution equipment is located in an un-classified location. One transformer and one 400a panel are located within the classified location boundries. These are each fed by underground raceways from the DP and are located on the wall that defines the division between the classified and un-classified areas. The classified location is governed under art. 511. The installation of the feeder conduit is as follows:
1) 90 dergee bends were made in full sticks of GRC so that no fitting is below 30" above the floor in the classified location.
2) 10' lengths of conduit were used, and the direction of the underground system led away from the above classified location, thus the transition to PVC conduit is some 5' beyond the wall seperating the two locations and under the un-classified area.
My take on this installation is that art. 501-5 (b)(2) Exception No. 1 applies and no seal-offs are required.
I'm currently "discussing" this issue with the AHJ, who seems to find a violation, and wants to see seal-off fittings.
Your input would be appreciated. Thanks