17-75 Log #580 NEC-P17
Final Action: Reject
(680.10)
__________________________________________________ __________
Submitter:
Michael Tooke, Temecula, CA
Recommendation:
This article as currently written:
Underground wiring shall not be permitted under the pool or within the area
extending 1.5 m (5 ft) horizontally from the inside wall of the pool unless this
wiring is necessary to supply the pool equipment permitted by this article.
Where space limitations prevent wiring from being routed a distance 1.5 m (5
ft) or more from the pool, such wiring shall be permitted where installed in
rigid metal conduit, intermediate metal conduit, or a nonmetallic raceway
system. All metal conduit shall be corrosion resistant and suitable for the
location. The minimum burial depth shall be as given in Table 680.10.
This article with the revision:
Where space limitations prevent wiring that is necessary to supply the pool
equipment from being routed a distance 1.5 m (5 ft) or more from the pool,
such wiring shall be permitted where installed in rigid metal conduit,
intermediate metal conduit, or a nonmetallic raceway system. All metal conduit
shall be corrosion resistant and suitable for the location. The minimum burial
Substantiation:
The first sentence in this article states that NO underground
wiring is permitted within 1.5 m (5 ft) from the inside wall of the pool unless it
is necessary to supply pool equipment. The next sentence needs clarification, as
it is being interpreted that ANY underground wiring (even if it is not necessary
to supply the pool equipment) is permitted within the 1.5 m (5 ft) area so long
as it is installed in an approved raceway at the depths listed in the chart. By
adding the phrase that is necessary to supply the pool equipment to this second
sentence (where I indicated above), it clarifies the intent of the article.
Panel Meeting Action: Reject
Panel Statement: The intent of the Code is to permit, when space is limited,
conduits from other systems to be buried within 5 ft of the pool in accordance
with 680.10 and Table 680.10.
Number Eligible to Vote: 11
Ballot Results: Affirmative: 11