Have a 2p-20a breaker(2#12’s) feeding a 100a disconnect fora unit heater. The unit heater is about 2 Kw. How/why could there be a 100adisconnect? Thanks.
 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Semi-Retired Electrical Engineer
It's overkill, but not an issue. The disconnect has to be rated to handle the current that will be sent through it. So it will see under 10 amps and has the ability to handle ten times that. Someone spent too much money on that disconnect. But there is no safety hazard and no code violation.
 

mstrlucky74

Senior Member
Location
NJ
So the disconnect serves as a manual means of disconnect only....not for fault, short circuit etc.?